If the core losses are 20 watts at rated load, the core losses at 50% load and 0.8 pf is:?

answers to choose from:

20W, 15W, 12W, 16W

Update:

please explain how to do it

2 Answers

Relevance
  • Bony
    Lv 5
    1 decade ago
    Favorite Answer

    ** The core losses remain at 20Watts. = Answer

    The two losses usually considered are,

    1. Iron or core losses. These do not change

    significantly with load changes. As this is the

    type of loss the question asks about, the answer

    is that there is no change between full and 50% load.

    So 20W losses at FL, still = 20W losses at 50% load.

    For related interest,

    2. The other losses are copper losses, also

    called I²R losses. Note I²R equates to Watts.

    There losses relate to the square of the load change.

    Assume 60W FL copper losses.

    Then at half load copper losses = (0.5)² * 60 = 15Watts.

    Then at 1/4 load copper losses = (0.25)² * 60 = 3.75Watts.

    Then at 120% load copper losses = (1.2)² * 60 = 86.4Watts.

    • Commenter avatarLogin to reply the answers
  • Jacy
    Lv 7
    1 decade ago

    For a transformer and motors the core losses are constant & independent of load.

    Try 20*0.8 = 16 W

    • Commenter avatarLogin to reply the answers
Still have questions? Get your answers by asking now.